Condensing vs Non-Condensing Tankless Water Heater: Efficiency, Venting, and Cost
Both types heat water on demand with gas. But a condensing tankless water heater also pulls extra heat from the exhaust, often with a second heat exchanger. That extra step raises efficiency, and it also changes how the unit vents and drains. A non-condensing tankless model is simpler, but it sends much hotter exhaust out the vent. This guide looks at the condensing vs non-condensing tankless water heater choice. It covers efficiency, venting, condensate, and install cost. It also explains ENERGY STAR's bar and the small power load many gas models need in outages.
Condensing vs Non-Condensing Tankless Water Heater: Key Differences
Have you ever looked at two tankless units with similar flow ratings and wondered why one costs more? The difference comes down to heat recovery. A condensing unit captures heat from its exhaust gases. It cools them so much that water vapor turns into liquid. That one change affects the vent, the drain, and the efficiency rating.
How Each Design Handles Exhaust Heat
A non-condensing unit has one heat exchanger. It sends the exhaust straight outside. A. O. Smith's condensing vs non-condensing comparison puts that exhaust at 300 to 500°F. A condensing unit recovers additional heat from exhaust until water vapor condenses. Many designs use a secondary exchanger, while some use one multi-pass exchanger. A. O. Smith gives about 100 to 120°F as an example of condensing exhaust temperature. Check the specific model for venting requirements.
That cooling creates condensate, which A. O. Smith describes as slightly acidic. It notes that stainless steel resists that acid better. That matters for how long the heat exchanger lasts.
Condensing
Non-condensing
Heat exchangers
Usually two (the secondary recovers exhaust heat); some use one with multiple passes
One
Exhaust temperature (A. O. Smith)
About 100 to 120°F after the secondary exchanger
About 300 to 500°F
Vent material
Often PVC, per A. O. Smith; confirm in the model's manual
Metal, such as stainless steel or suitable aluminum, per A. O. Smith; confirm in the manual
Condensate handling
Heat exchanger drain required; some installs add a pump or neutralizer
No heat exchanger drain; some vent layouts need a vent condensate collector and trap (e.g., Rinnai RE vertical runs), per the manual and local code
Typical UEF (A. O. Smith)
Above 0.90; models at 0.95 or higher can meet ENERGY STAR
About 0.80 to 0.82
What ENERGY STAR Requires
Do you want a certified model? Then the efficiency bar decides which type qualifies. ENERGY STAR's water heater key product criteria list the rules. Gas tankless models need a Uniform Energy Factor (UEF) of 0.95 or higher. They need at least 2.8 gallons per minute over a 67°F temperature rise. The warranty must cover at least 6 years on the heat exchanger and 5 years on parts. Non-condensing models rate around 0.80 to 0.82, so they fall short. In practice, the label points you toward a condensing design.
Tankless Water Heater Venting Comes From the Manual
Tankless water heater venting isn't one size fits all. Vent material, direction, length, and end point follow your model's manual and local code. Treat the table as a general pattern.
Before you pick a type, weigh the pros and cons of tankless designs as a whole. Both types also share a trait that surprises many homeowners. Many gas tankless units need electricity to run.
Do Gas Tankless Water Heaters Work Without Power?
Picture a winter storm knocking out power on a Sunday morning. You might expect a gas tankless heater to keep the showers going, since the gas line still works. For many models, that's not how it plays out.
A. O. Smith says its gas tankless units need electricity to run the electronic ignition, control board, display, and safety systems. So they stop working during outages. The condensing step doesn't change that. Check the manual whichever type you choose.
Not every gas tankless unit works this way, though. Bosch's Therm 520 HN spec sheet says that model uses hydro-power ignition. It runs without a standing pilot, an electrical connection, or a battery. So outage performance depends on the model, not just the fuel.
How Much Power a Gas Tankless Unit Draws
For models that do need power, the load is small. A. O. Smith lists about 100 to 150 watts for a few seconds at startup on its models. After that, they use 60 to 100 watts while running. Your own heater may differ, so use the figures in its manual. Some installs also have a condensate pump. If yours does, add its labeled watts.
Gas Tankless Water Heater PowerGas Tankless Water Heater Power
Check These Things Before Using Backup Power
Start with your heater's manual. Confirm each of these details:
  • Plug-in or hardwired: A. O. Smith says its units plug into a grounded 120V outlet. Or they're wired to a dedicated circuit. A plug-in model is a candidate for direct connection only if its manufacturer approves the specific off-grid supply and all electrical requirements are met. A hardwired unit needs a licensed electrician and a suitable transfer device.
  • Direct cord only: For a plug-in heater explicitly approved for the specific backup supply, use the manufacturer’s prescribed cord and outlet arrangement. Some manuals ban extension cords and adapter plugs, so check yours. The CDC warns against connecting generators to home circuits without approved automatic-interrupt devices.
  • Maker approval and grounding: Does your manual skip battery backup or the outlet type? Ask the maker before you plug in.
  • Gas and water supply: Backup power doesn't supply gas or create water pressure.
Does your heater check those boxes? Then start with the outlet rule. A. O. Smith says its plug-in units should go into a grounded 120VAC, 60Hz outlet. When used off grid, EcoFlow describes the DELTA 3 Classic as a floating-ground system. That outlet arrangement does not by itself establish that the heater’s grounding and ignition-sensing requirements are met.
So a matching plug and enough watts aren't proof that a heater will run safely. A licensed electrician or the heater's service tech should check grounding, live and neutral wiring, and ignition sensing for your exact model first.
If the heater manufacturer confirms compatibility with this off-grid output and the electrician verifies the required configuration, the EcoFlow DELTA 3 Classic is one option for that small, steady load. EcoFlow lists 1,024Wh of LFP battery capacity and 1,800W of pure sine wave AC output. That's well above the fan, controls, and igniter load on A. O. Smith's example models. The heater can then keep running for a limited time, depending on battery capacity and the actual load.
EcoFlow DELTA 3 Classic (1024Wh) + Bag
•Fast AC Recharging: Reaches 0 to 80% in 45 minutes from a standard wall outlet, with 4 charging methods in total. • 1,800W Output: 3,600W surge, and up to 2,600W with X-Boost for compatible devices such as some microwaves and window AC units. Check each device's wattage first. • 10ms Auto-Switch: Switches to battery power within 10ms for devices plugged directly into the unit, such as a Wi-Fi router or NAS.
How Long Could a Battery Last?
These runtimes are estimates, not promises. They assume about 85 percent of the battery is usable and use the top of A. O. Smith's running range.
Example load
Watts used
EcoFlow DELTA 3 Classic (870Wh usable, estimate)
A. O. Smith gas tankless example while running (60 to 100W; 100W used)
about 100W
about 8.7 hours at a constant 100W (theoretical)
The 8.7 hours is simple math for one steady load, not a forecast for a real outage. Some heaters use power even when no tap is open. A. O. Smith's ADAPT gas tankless manual says its freeze protection uses heating blocks plus an autofire mode that runs the burner for a short time. That system only works when the unit has electrical power.
Rinnai's RE series installation manual says that the freeze protection depends on continued electrical and gas service and is subject to the manual’s temperature and installation limits. Its spec table also lists separate standby and freeze protection power figures. Recirculation and condensate pumps add their own loads.
So a low draw between showers only applies to models and conditions without those extra loads. For a cold-weather outage, add standby, freeze protection, recirculation, and condensate pump power from your own model's manual. You can learn more about tankless water heater battery backup before the next outage.
Efficiency and Operating Cost
Are you trying to figure out whether the extra efficiency will show up on your gas bill? Condensing units use less gas to deliver the same hot water. How much you save depends on how much hot water your household uses and how cold your incoming water is.
Tankless Water Heater Operating CostsTankless Water Heater Operating Costs
What UEF Means for Your Gas Bill
Gas tankless efficiency is rated by UEF. A higher number means more of the fuel's energy ends up in your hot water instead of going out the vent. According to A. O. Smith, non-condensing models typically rate around 0.80 to 0.82. Condensing models usually rate above 0.90, and most fall between 0.90 and 0.98. Much of that gap is exhaust heat. A non-condensing unit sends it up the vent, while a condensing unit keeps it.
When Condensing Pays Off More
Climate plays a big part. A. O. Smith notes that colder incoming water makes the condensing edge bigger. Homes in warm climates see less payback. A large family in Minnesota usually gains more than a couple in Phoenix. Household size matters too. More showers, laundry loads, and dishwasher cycles give the higher UEF more chances to save gas.
How to Compare Models
Start with the UEF on each model's label or spec sheet. Then compare these factors side by side:
  • UEF rating
  • Flow rate in gallons per minute at your winter temperature rise
  • Your household's daily hot water use
  • Local natural gas or propane prices
  • Available utility rebates
If two models have close UEF ratings, the one with the simpler install may come out ahead. That's why install pricing matters so much.
Even an efficient gas unit may still rely on household power, though. Before storm season, check whether gas water heaters need electricity in your home. Efficiency is also only half the cost picture. Installation can tip the decision too.
Installation Cost Differences
Two quotes for tankless water heaters can look far apart. That happens even when the units have similar flow ratings. A. O. Smith says non-condensing models cost less upfront than condensing ones. Condensing units can often vent with PVC. A. O. Smith calls it cheaper per foot and easier to route. But condensing units also need a drain.
When a Non-Condensing Unit Makes More Sense
Are you replacing an older gas water heater? A. O. Smith says you may be able to reuse your old heater's metal venting if it's compatible. A plumbing pro should confirm it first. That can trim the venting part of the bill.
Location matters too. A. O. Smith notes that non-condensing units work well on exterior walls. They also suit spots where a new drain line would run through several rooms. A non-condensing heater usually has no dedicated heat-exchanger drain, but the vent may still need a condensate collector or drain. Ask your installer to compare the complete venting and drainage costs.
What to Itemize in Every Quote
Ask each installer to break out the job instead of giving one lump sum. A full quote should list:
  • The water heater itself
  • Venting material, length, and termination
  • Gas line work, including any upsizing
  • Condensing-unit drain or pump, plus vent condensate collection or drainage if the model and vent layout require it
  • Condensate neutralizer, if local code requires one
  • Electrical work, such as a nearby outlet or dedicated circuit
  • Permits, inspection, and removal of the old heater
Planning the Condensate Drain
Every condensing tankless water heater needs a condensate drain. Some local codes require a small neutralizer tank, A. O. Smith notes. It treats the acidic condensate before it reaches your drains. Dispose of condensate as your model's manual and local code require. Ask your installer about these rules before you sign a quote, so the drain work is priced in from the start.
If no drain sits nearby, your installer may add a condensate pump. That adds cost and one more device that needs power. Open to electric? You can also compare heat pump water heater efficiency before you commit to new gas work.
Long-Term Upkeep
The cost doesn't stop at installation day. A. O. Smith says tankless heaters last 15 to 20 years with regular care. The main task is descaling. That clears mineral deposits from the heat exchangers. Homes with hard water may need it as often as twice a year.
Condensing models add one more chore. Check the drain line and any neutralizer from time to time. Check any required vent condensate collector or drain on a non-condensing model as directed by its manual. Talk to a professional installer about your home before you choose.
The condensing vs. non-condensing tankless water heater choice comes down to heat recovery. Condensing units can meet ENERGY STAR's 0.95 UEF bar, but they need a condensate drain. Non-condensing units are simpler and cost less upfront. Compare UEF ratings, venting, and full quotes before you decide. Does your gas model rely on outside power? The EcoFlow DELTA 3 Classic can supply a compatible plug-in heater for a limited time after the heater manufacturer and a licensed electrician confirm the specific off-grid configuration. How long depends on battery capacity and the actual load.
What is the difference between condensing and non-condensing tankless?
A condensing unit recovers exhaust heat and produces condensate in the unit. That can be done with two exchangers or one multi-pass exchanger. A non-condensing unit vents hotter exhaust and usually has no dedicated heat-exchanger drain; some vent layouts still need condensate collection and drainage.
Is a condensing tankless water heater worth it?
It often pays off best in homes with high hot water use or cold incoming water. Compare each model's UEF against the full installed cost, including venting and drainage.
Do condensing tankless heaters need a drain?
Yes. Their slightly acidic condensate has to drain away as the manual and local code require. Some homes also need a neutralizer or pump.
Do gas tankless water heaters need electricity?
Many do, for ignition, controls, and the fan, so they stop in an outage without backup power. Some models, such as the Bosch Therm 520 HN, use hydro-power ignition instead.
What efficiency does ENERGY STAR require?
ENERGY STAR requires gas tankless water heaters to reach a UEF of 0.95 or higher. Certified models also need at least 2.8 gallons per minute over a 67°F rise and a 6-year heat exchanger warranty.
Home Solutions